    Thursday, November 5, 2026 5:32:39 AM
    Choosing a 3 Phase AC Current Sensor for Motor Monitoring
    Hey everyone,
    I’m a research assistant at a university, working on a project where I need to measure AC current on a 3-phase cable supplying an electric motor. The measured current data will be sent to a microcontroller. Since I’m a mechanical engineer with limited experience in electronics, I could use some advice on selecting a suitable sensor.
    The motor typically runs between 30A and 50A, but during startup, it can spike up to 450A. I’d prefer a sensor with a DC 0-5V or DC 0-4mA output, and ideally, it should run on a 12VDC supply (though this isn’t a strict requirement). I was looking at the ATO-CUS-3AC80 and ATO-CUS-AC1500 but wasn’t sure if they were suitable. Any recommendations?
    William wrote:
    Hey everyone,
    Based on your requirements, I'd recommend the ATO-CUS-3AC80 model. It measures up to 80A with 0.5%FS accuracy, which should work well within your typical range. Let us know if you have any other questions!
    William wrote:
    Hey everyone,
    The ATO-CUS-3AC80 looks fine for your steady-state currents, but your startup current of 450A is a concern. If the sensor saturates at 80A, it won't capture the inrush current properly. If startup current monitoring is critical, you might need a sensor with a higher range, or a dual-sensor setup—one optimized for normal operation and another for startup conditions.
    Hey everyone,
    The motor typically runs between 30A and 50A, but during startup, it can spike up to 450A. I’d prefer a sensor with a DC 0-5V or DC 0-4mA output, and ideally, it should run on a 12VDC supply (though this isn’t a strict requirement). I was looking at the ATO-CUS-3AC80 and ATO-CUS-AC1500 but wasn’t sure if they were suitable. Any recommendations?Based on your requirements, I'd recommend the ATO-CUS-3AC80 model. It measures up to 80A with 0.5%FS accuracy, which should work well within your typical range. Let us know if you have any other questions!
    Thanks for the insights! That helps a lot. I do have one more question about the "overload capacity" listed in the datasheet. It says "30 times nominal input." Does this mean the sensor can handle up to 2400A for a short time? If so, how long can it withstand that overload?
    Good question! The overload capacity refers to the sensor's instantaneous limit. It can handle up to 2400A for a very short duration—about 4-5 seconds max before potential damage occurs. It's not meant for continuous operation at those levels.