Dennett wrote:Hi, we had a
GK3000-1S0022 3 hp (2.2 kW) single phase VFD for use with a 230V 1P 10.6A single phase motor. I have set it up following the instructions. We get error E1 when connected to U&V, and we get error E3 when connected to U&W.
Hi, Dennett
Please follow the steps below to check and reset the VFD parameters:
1. Capacitors can be maintained when wiring single-phase motors, and just connect the 2 power wire of the motor to U, V or U, W.
2. The nameplate of your single-phase motor shows that the motor supports multiple input voltages. Please check the wiring instructions of the motor to confirm that the wiring is connected according to single-phase 220V or 230V.
3. If the motor wiring is confirmed to be correct, please set P3.01=10 (restore the factory parameter settings), and then reset the VFD parameters according to the attached quick setting document, and try testing again.