    5 kVA Single Phase Frequency Converter Output Voltage Issue

    2 months ago
    #203 Quote
    Hello, everybody! Our HZ-50-1105 5 kVA single phase frequency converter has no output voltage. The display for voltage and frequency are both 0. The converter has been working until recently. As we turned the converter on, there would be a warning buzzer. We confirmed there is input voltage and we also tried to replace the fuse but there is no output voltage. Do you have any recommendations on what else we can check?
    0
    2 months ago
    #204 Quote
    Alexander wrote:
    Hello, everybody! Our HZ-50-1105 5 kVA single phase frequency converter has no output voltage. The display for voltage and frequency are both 0. The converter has been working until recently. As we turned the converter on, there would be a warning buzzer. We confirmed there is input voltage and we also tried to replace the fuse but there is no output voltage. Do you have any recommendations on what else we can check?

    It sounds like the warning buzzer might indicate a fault with the driver board. I'd suggest checking if the IGBT (Insulated Gate Bipolar Transistor) module is functioning correctly. Sometimes, low or no output voltage can be due to issues with the IGBT or the driver circuitry.
    0
    2 months ago
    #205 Quote
    Alexander wrote:
    Hello, everybody! Our HZ-50-1105 5 kVA single phase frequency converter has no output voltage. The display for voltage and frequency are both 0. The converter has been working until recently. As we turned the converter on, there would be a warning buzzer. We confirmed there is input voltage and we also tried to replace the fuse but there is no output voltage. Do you have any recommendations on what else we can check?

    The single phase frequency converter has a warning buzzer, which may be a fault with the driver board. Please now follow the attached troubleshooting document to measure the IGBT module and driver board, and feedback with the measurement results for the next step.
    0
    ATO.com
    2 months ago
    #206 Quote
    ATO wrote:
    The single phase frequency converter has a warning buzzer, which may be a fault with the driver board. Please now follow the attached troubleshooting document to measure the IGBT module and driver board, and feedback with the measurement results for the next step.

    Thank you for the response! Below are the measurements following the 5kVA converter troubleshooting document. The N-G2 DC voltage is very low.
    Fuse resistance: 0.1 ohm
    IGBT module detection:
    L-G1: 9.99 KΩ
    L-G2: 9.99 KΩ
    N-G1: 10.01 KΩ
    N-G2: 10 KΩ
    Driver board checkers:
    J1: 25.22 VAC
    J2: 25.2 VAC
    J3: 25.22 VAC
    J4: 25.17 VAC
    L-G1: 1.451
    DCV L-G2: 1.288 DCV
    N-G1: 1.356 DCV
    N-G2: 0.689 DCV
    We are currently lining down because of the converter. We would appreciate your help with troubleshooting.
    0
    2 months ago
    #207 Quote
    The issue appears to be within the N-G2 cell. I verified that the N-G2 connector was inserted properly and cleaning the contact pins did not make any difference. I could only perform the visible inspection on the top of the PCA and I could not see any burnt spots or components. I would appreciate any additional troubleshooting instructions you can offer.
    0
    2 months ago
    #208 Quote
    Alexander wrote:
    Thank you for the response! Below are the measurements following the 5kVA converter troubleshooting document. The N-G2 DC voltage is very low.
    Fuse resistance: 0.1 ohm
    IGBT module detection:
    L-G1: 9.99 KΩ
    L-G2: 9.99 KΩ
    N-G1: 10.01 KΩ
    N-G2: 10 KΩ
    Driver board checkers:
    J1: 25.22 VAC
    J2: 25.2 VAC
    J3: 25.22 VAC
    J4: 25.17 VAC
    L-G1: 1.451
    DCV L-G2: 1.288 DCV
    N-G1: 1.356 DCV
    N-G2: 0.689 DCV
    We are currently lining down because of the converter. We would appreciate your help with troubleshooting.

    Based on your feedback and the measurements provided, it appears the driver board is damaged. The voltage discrepancies, particularly in the N-G2 readings, suggest a fault on the board itself. You will need to replace the driver board with a new one to resolve the issue.
    0